wwhitney
- Berkeley, CA
- Retired
Example D7 concerns the use of 310.12, the 83% "factor" for sizing residential services/main feeders. It start by noting that for a 175A rated service, if no ampacity correction or adjustment is required, only 145A of ampacity is required, so at least 75C rated #1/0 Cu or #3/0 Al would suffice.
It then considers the case of XHHW-2 conductors (which have 90C rated insulation) installed in a 38C ambient environment, which gives 0.91 ampacity correction factor. That means the required tabular ampacity is 175*83%/0.91 = 160A. But in translating that into conductor size, the example still uses the 75C column and gets #2/0 Cu or #4/0 Al.
As far as I can see, this is a mistake? Since the conductor insulation is rated 90C, we can use the 90C column, so the answer remains #1/0 Cu or #3/0 Al. That is, under the conditions given, the usable ampacity of #1/0 Cu will be the lesser of the 150A (the 75C ampacity, for terminations) and 170A * 0.91A = (the 90C ampacity, corrected for temperature). So #1/0 Cu still has a 150A ampacity, and suffices for the 175A residential service.
Am I missing something here? Or should I submit a PI?
Cheers, Wayne
Cheers, Wayne