I am an ESS installer and am in discussion with an AHJ about whether or not a locking device is needed for AC Coupled energy storage systems (ESS). I also want to understand more about when locking open is required, what satisfies this requirement? I am specifically looking at the Tesla Powerwall, but I imagine other AC Couples ESS are similar. We are under the 2017 NEC (2019 CEC)
These AC coupled Energy Storage Systems have a UL 1741 listed inverter as part of them, so they shutdown very quickly when the breaker that feeds them is opened. I understand this anti-islanding feature to be the reason why PV circuits are often not required by many AHJ to add a locking disconnect, though some still do require it.
When locking the disconnect is required by the AHJ, what sort of equipment satisfies the requirements of 110.25?
1. It is pretty clear that Bladed Disconnects are allowed, but they are a bit large and ugly. We could use them with only the aesthetic issues, but those are significant with many of our customers.
2. Locking the enclosure seems somewhat reasonable, except for 705.22 (3) indicates this won't allow the user to see whether the breaker is still in the off position.
3. Using add-on breaker accessories like the BRLW below should be compliant in my eyes, but the local AHJ will not allow it. They are requiring the bladed lockable disconnects only.
These AC coupled Energy Storage Systems have a UL 1741 listed inverter as part of them, so they shutdown very quickly when the breaker that feeds them is opened. I understand this anti-islanding feature to be the reason why PV circuits are often not required by many AHJ to add a locking disconnect, though some still do require it.
When locking the disconnect is required by the AHJ, what sort of equipment satisfies the requirements of 110.25?
1. It is pretty clear that Bladed Disconnects are allowed, but they are a bit large and ugly. We could use them with only the aesthetic issues, but those are significant with many of our customers.
2. Locking the enclosure seems somewhat reasonable, except for 705.22 (3) indicates this won't allow the user to see whether the breaker is still in the off position.
3. Using add-on breaker accessories like the BRLW below should be compliant in my eyes, but the local AHJ will not allow it. They are requiring the bladed lockable disconnects only.