I have read this best practices recommendation from a specific vendor we deployed here onsite:
"To maintain stability, no greater than 150% of the [ESS] continuous power capacity (in IQ PV capacity) can be wired into [the energy system]."
I have a 7 (@1.21Amp ea) microinverter system (240VAC*1.21A*7=2.017kWac)
The battery power capacity is spec'ed at 1.28kWac (1.28kWac*1.5=1.920kWac)
So 2.017>1.920 = violation
In the manuf. chart, they make it simple and do show 6 (@1.21A) inverters max with that single battery unit. To comply, I will temporarily disconnect one inverter/module combo from the string until the second 1.28kWac battery arrives, but what stability are they referring to specifically? I am assuming this is a general design recommendation for PV/ESS systems and not manuf specific.
"To maintain stability, no greater than 150% of the [ESS] continuous power capacity (in IQ PV capacity) can be wired into [the energy system]."
I have a 7 (@1.21Amp ea) microinverter system (240VAC*1.21A*7=2.017kWac)
The battery power capacity is spec'ed at 1.28kWac (1.28kWac*1.5=1.920kWac)
So 2.017>1.920 = violation
In the manuf. chart, they make it simple and do show 6 (@1.21A) inverters max with that single battery unit. To comply, I will temporarily disconnect one inverter/module combo from the string until the second 1.28kWac battery arrives, but what stability are they referring to specifically? I am assuming this is a general design recommendation for PV/ESS systems and not manuf specific.