Estimate of typical resisdential feed utility transformer secondary inductance
Hi Mivey,
Since I did not know what to do I followed the example at the site I posted a link to early on. Being aware of the dangers in relying on arbitrary internet sites ( coupled with my interpretation of same) I was looking for some help here.
The site referenced found a "Zbase" calculated from MVA and KV. From there they used the Zbase and %Z to find the impedance. I was not familiar at all with using "per unit" values that are common in the power distribution realm.
Would you please detail the method you use so that I may learn from it?
Thanks,
Ela
I used some approximate per-unit data to derive the values I posted. You assumed all reactance and you had a combined primary and secondary reactance because the transformer %Z is for the combination of primary and secondary impedance.
You can find approximate X/R ratios for different transformer sizes and use them to help with the X approximation when given %Z.
Example with 2.1%:
If we use 25kVA and 2.1%Z and look at the secondary side:
Zbase = V2 / S = 2402 / 25000 = 2.304 Ω
If we assume the X/R ratio is about 1.3 and the primary and secondary impedances are about equal on a per-unit basis we get:
Z122 = X122 + R122 = X122 + ((X12 / R12 ) / 1.3 * R12)2 = X122 + (X12 / 1.3)2
0.0212 = X122 + 0.7692 * X122
0.0212 = 1.592 * X122
X12 ~ sqrt(2.77E-4) = 0.016645 pu = 0.016645 pu * Zbase = 38.35 mΩ
X2 ~ X12 / 2 = 19.18 mΩ
Example with 2.6%:
If we use 25kVA and 2.6%Z and look at the secondary side:
If we assume the X/R ratio is about 1.4 and the primary and secondary impedances are about equal on a per-unit basis we get:
Z122 = X122 + R122
0.0262 = X122 + 0.7142 * X122
0.0262 = 1.51 * X122
X12 ~ sqrt(4.476E-4) = 0.021157 pu = 0.021157 pu * Zbase = 48.75 mΩ
X2 ~ X12 / 2 = 24.37 mΩ
Thank you very much Mivey for the detailed response.
I appreciate your willingness to share your knowledge.