Ethernet in a MCC raceway.
Montana
What I have is an Allen-Bradley MCC with Power Flex variable speed drives. I would like to communicate with these drives via 20-COM-E modules. This would require putting CAT-5 in the raceways with the motor leads. The motor leads are rate for 600V and the CAT-5 is only rated for 300V. I?ve done a bunch of searches and read a bunch of threads and I still can?t figure out if this is acceptable. Any help would be greatly appreciated.
Montana
In my searches I came across a thread called, ?Devicenet Cables within the same Wireway as 600 Volt motor powerwires? This thread address a lot of similar issues.
Montana
In my searches I came across a thread called, “Devicenet Cables within the same Wireway as 600 Volt motor powerwires” This thread address a lot of similar issues.
don_resqcapt19
Illinois
retired electrician
Just put a length of flexible metal conduit in the MCC wireway and install the Ethernet in the flex.
I don't really think fiber is a real option here. The communications is being run to multiple buckets in the MCC. There is not likely enough space for the media converters and their power supplies.
don_resqcapt19
Illinois
retired electrician
091119-1922 EST
Montana:
Consider Ethernet to fiber and run the fiber with the high voltage. Even if you had high voltage Ethernet cable I would be concerned with noise problems.
The construction of the Ethernet cable does a lot to protect it from the "noise". I am aware of a number of installations with standard Ethernet cable in the MCC wireways for PLC control of the equipment and I have heard of any noise issues.
gar
091120-0914 EST
Don:
Your information is useful because it relates a similar application.
Ethernet cables use twisted pairs. This greatly reduces magnetic coupling of noise to the balanced signal lines. They also use different pitches of the twist for the four different pairs to reduce crosstalk.
In crude uncontrolled experiments I have run with Ethernet communication with CAT-5 cable using a MIG welder as the noise source I found degradation of the signal, meaning retries, when the CAT-5 cable was in the range of about 3 to 4 ft of the MIG welder cables.
Montana
Thanks to all of you. It?s nice to have a place to post a question to experts in the field. I can?t even imagine the years of experience that went into these replies. I can see this is a gray area that the NEC needs to address. Again thanks for all the replies.
Some where in Montana
Actually the NEC had already addressed it. It claims no authority inside electrical equipment.