Is there anything required (other than the cable) in Chapter 8 for a shed that has ethernet run from a switch in the main house?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't see a need. You are using just plain cat 6 I presume but I am unaware of a sheathed cable that you could bond to the grounding electrode conductor, if needed.
 

paulengr

Senior Member
Yes, Cat 6 which is unshielded.

CAT 6 comes in UTP and ScTP. Depends on what you order.

Ethernet transceivers use isolation transformers at both ends with 1500 V of isolation and the signal is both purposely designed to be over 100 Hz and filtered below that to avoid any interference with noise from power lines. So grounding for noise is utterly pointless. Shielding increases the already considerable 30 dB SINR up another few dB from electrostatic fields but decreases it a few dB against magnetic fields such as those generated by motors and transformers.

Best practice is just use fiber but for homeowner situations paying someone to terminate it and the extra cost of fiber switches may not be worth it. These days mesh networks work so well though that it’s cheaper just to get some meshing WiFi radios and enjoy coverage both inside and out on the lawn. I prefer Ubiquity but that’s professional grade. TP Link is a close second. Google has proven themselves not trustworthy.
 
Best practice is just use fiber but for homeowner situations paying someone to terminate it and the extra cost of fiber switches may not be worth it.
Pre-terminated fiber and media converters do the job. Depends on the distance needed- 100'? CAT6 or 5; 300'? I'd go fiber even if it's in-spec for copper (and the installation cost is going to well exceed the materials/electronics).

A quick search turned up https://www.fiber-mart.com/- 50M Singlemode 6 Fiber LC/FC/SC/ST Pulling eye Pre-terminated Fiber Cable US$120.00 which is a rather decent price; longer cables available.

These days mesh networks work so well though that it’s cheaper just to get some meshing WiFi radios and enjoy coverage both inside and out on the lawn. I prefer Ubiquity but that’s professional grade. TP Link is a close second.
They make what's effectively a "consumer" level, but in any case, you're playing for quality and support; they're kind of like the Apple of wireless networking :D.

Google has proven themselves not trustworthy.
Works for me all the time.
 

mikeames

Senior Member
Location
Gaithersburg MD
Occupation
Teacher - Master Electrician - 2017 NEC
My concern would be for 6A shielded if the shed had power. If there is no power in the shed then no issue with anything. If there is power then UTP is no issue. Adding a shield as in 6A would complicate it a bit, but I have read the shield should only be bonded at one patch/ switch.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Adding a shield as in 6A would complicate it a bit, but I have read the shield should only be bonded at one patch/ switch.
In audio, a shield connected at only one end is normally done so at the receiving end, so the entire group of equipment upstream doesn't become part of the signal
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is there anything required (other than the cable) in Chapter 8 for a shed that has ethernet run from a switch in the main house?
That would be covered by Article 725 and nothing special unless the cable is exposed to lightning. That would trigger 725.41.
725 applies to data and phone cables on the load side of the first customer owned piece of equipment.
 

mikeames

Senior Member
Location
Gaithersburg MD
Occupation
Teacher - Master Electrician - 2017 NEC
In audio, a shield connected at only one end is normally done so at the receiving end, so the entire group of equipment upstream doesn't become part of the signal
That makes sense, and from what I read its the same reason. Keep the shield as a shield and not risk having any current flow on the shield between the two points.
 