I was possibly a bit too vague, but that's what I meant. Our tables are very simple compared to what most EU countries use.
Possible true - I don't have a copy of your code.
I don't know what other EU countries (we all oght to be the same although my experience suggests otherwise) but here in UK we use BS7671, commonly known as "The Regs".
Taking 25mm
2 as an example:
From table 4D1A which is for single core 70C pvc non-armoured and 30C ambient, we get current ratings of
80, 73, 101, 89, 114, 104, 126, 112, 146, 130, and 110
The 73A rating is for 3-phase in conduit in a thermally insulating wall.
For free air, horizontal, flat spaced you get 146A.
Take the ambient up to 40C for this type of cable and you have to apply a 0.94 correction factor.
Use a semi-enclosed fuse (who does these days?) and you have to apply I
n/(0.725*C
a*C
r)
Stick it in a trench with as many different geometric layouts as a Rubic's Cube could generate....
Table 4D2A, multicore pvc non-armoured gives you a different set of values.
Make it multi-core armoured and another lot of readings.
Then there is single-core (non-magnetic) armoured.
Make it XLPE and you get another set of tables.
With mineral unsulated (MI), a whole different bunch of stuff.
Repeat for Al instead of Cu.....
I think it sounds a lot more complicated than it is in practice - it covers all possible eventualities.
In reality, aluminium conductors are rarely use. We never do. So, to all intents and purposes, that takes out half the bumf at a stroke.
MI is used for fire alarms and maybe some other specialist applications. Another whole chunk out of the way. For us.
It's probably easier to say what we commonly use.
For our panels, the control wiring is mostly 1.0mm
2 in various colours depending on function. They are run in open slot PVC trunking to keep it neat.
Signal wires (encoders etc) are screened. Comms Cat5.
Power cables are single core and in free air. Or copper bar for high current.
Externally, everything is run in multi-core steel wire armoured.