I can easily gather data regarding core size versus ?ampacity? for US ?AWG? wire sizes. There is the ?NEC National Electrical Code? document and hundreds of Google hits with articles, tables, and on-line calculators.
But I am having a much more difficult time finding information on any of the European standards like CENELEC, BS7671, or even the Canadian CE. Is anyone familiar with any such standards? If so, could you point me in the right direction?
For example, here is a tiny portion of NEC table 310.16 AWG standard for wire ampacity:
Size / 60C / 75C / 90C
8AWG 40 50 55
6AWG 55 65 75
4AWG 70 85 95
The insulation temp rating columns give the data that I am looking for. They give the maximum allowable electrical current (in Amperes) that each wire size can safely carry for each of three different wire insulation temperature ratings (60, 75, and 90 degrees Centigrade).
But for any European standard, this is about all I have been able to come up with (example below), and I am not even sure that the 75C column is correct or even exactly what standard it might conform to... or even if these standards deal with temperature categories or categories in these ranges (i.e. 60/75/90).
Size / 60C / 75C / 90C
10MM2 ? 53 ?
16MM2 ? 71 ?
25MM2 ? 94 ?
Any suggestions you can give me will be greatly appreciated.
Many thanks,
Nate.
But I am having a much more difficult time finding information on any of the European standards like CENELEC, BS7671, or even the Canadian CE. Is anyone familiar with any such standards? If so, could you point me in the right direction?
For example, here is a tiny portion of NEC table 310.16 AWG standard for wire ampacity:
Size / 60C / 75C / 90C
8AWG 40 50 55
6AWG 55 65 75
4AWG 70 85 95
The insulation temp rating columns give the data that I am looking for. They give the maximum allowable electrical current (in Amperes) that each wire size can safely carry for each of three different wire insulation temperature ratings (60, 75, and 90 degrees Centigrade).
But for any European standard, this is about all I have been able to come up with (example below), and I am not even sure that the 75C column is correct or even exactly what standard it might conform to... or even if these standards deal with temperature categories or categories in these ranges (i.e. 60/75/90).
Size / 60C / 75C / 90C
10MM2 ? 53 ?
16MM2 ? 71 ?
25MM2 ? 94 ?
Any suggestions you can give me will be greatly appreciated.
Many thanks,
Nate.