A machine showed up in our shop that was bought by an ME from a french company.
We have 480V 3-ph; the machine has european cord and plug for 230V 1-ph. Internal conductors (serviceable) are labeled L* and N* with dual-pole fuse blocks where the L* have fuses and the N* have trapped shorting bars. So to change a fuse on an L conductor you break both L and N.
I'm thinking I have to refit this machine with dual-pole blocks both fused and leave N floating or replace with single-pole blocks for L and terminal strips for N and ground N.
I'm contacting the home company to see if floating/grounding of N is important. Third-party conversations gave rumor they expected us to just replace the european plug with a 240V appliance plug.
Any advice?
We have 480V 3-ph; the machine has european cord and plug for 230V 1-ph. Internal conductors (serviceable) are labeled L* and N* with dual-pole fuse blocks where the L* have fuses and the N* have trapped shorting bars. So to change a fuse on an L conductor you break both L and N.
I'm thinking I have to refit this machine with dual-pole blocks both fused and leave N floating or replace with single-pole blocks for L and terminal strips for N and ground N.
I'm contacting the home company to see if floating/grounding of N is important. Third-party conversations gave rumor they expected us to just replace the european plug with a 240V appliance plug.
Any advice?