Hi,
I have a question regarding using a neutral wire or not. My customer does not have a adapter for his EV that is 30 amp no neutral. Nema 6-30.
I was wondering if I can use a 50 amp NEMA 6-50 and place on a circuit run with #6 but using only a 30 amp breaker. The wire is upsized because the customer requested for to future proof.
So can I place a 50 amp receptacle on a circuit which wire ampacity is 60 but the breaker is only 30.
Thanks.
I have a question regarding using a neutral wire or not. My customer does not have a adapter for his EV that is 30 amp no neutral. Nema 6-30.
I was wondering if I can use a 50 amp NEMA 6-50 and place on a circuit run with #6 but using only a 30 amp breaker. The wire is upsized because the customer requested for to future proof.
So can I place a 50 amp receptacle on a circuit which wire ampacity is 60 but the breaker is only 30.
Thanks.