EV charger run neutral or not dilemma

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Hi,
I have a question regarding using a neutral wire or not. My customer does not have a adapter for his EV that is 30 amp no neutral. Nema 6-30.
I was wondering if I can use a 50 amp NEMA 6-50 and place on a circuit run with #6 but using only a 30 amp breaker. The wire is upsized because the customer requested for to future proof.

So can I place a 50 amp receptacle on a circuit which wire ampacity is 60 but the breaker is only 30.

Thanks.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
That's two questions.

In my opinion, a receptacle should have all terminals connected as expected, especially the neutral (and EGC).

I know you can't use a lesser receptacle, but I think you also need the circuit to be able to supply its rating.
 

retirede

Senior Member
Location
Illinois
Most EVSEs are either equipped with a 14-50P or a choice between a 14-50 and a 6-50. Not many 6-50 only.

The most flexible “future-proof” installation would be a 14-50R on a 50A circuit. I can’t really tell by your description of the customer’s current equipment if that would work now?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
The most flexible “future-proof” installation would be a 14-50R on a 50A circuit.

It seems electric-clothes dryer instructions don't allow the 30A appliance to run on 50A fuses.

If 30A clothes dryer appliance & 50A charger must use the same outlet, a 50A breaker/branch circuit only works if another plug box is used with fuse block for the 30A dryer plug.

See integrated 24 Amp circuit breaker built-in to the transfer switch below.

 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
So it supplies what should be an isolated neutral from the dryer receptacle's bonded neutral? Is that Kosher?

1644863140371.png
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
That's two questions. :)

In my opinion, a receptacle should have all terminals connected as expected, especially the neutral (and EGC).

I know you can't use a lesser receptacle, but I think you also need the circuit to be able to supply its rating.
This is a new circuit run in conduit. The run is over 100' with obstacles. So I ran 1/2 with the intention of running 2 #6 and use the conduit as ground to save a few dollars. The customer wanted to future proof with 60 amp wire if down the road has a service upgrade as he is close as he has electric heat.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
So it supplies what should be an isolated neutral from the dryer receptacle's bonded neutral? Is that Kosher?

View attachment 2559441

Ideally NEMA 14-30R outlets are available for 4-wire dryer circuits, so separate neutral and grounds can be properly connected.

For those existing 3-wire dryer circuits missing separate grounding, that Split-Volt 14-50R would be missing a nuetral.

The fact that Tesla doesn't use that white neutral for level two chargers doesn't help it pass inspection. Tesla defers to the AHJ's for the Building Wiring and outlets.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
IMO, if you use a receptacle that has a neutral in it, you should run a neutral to it. I am not sure it is specifically code required.

Here is a wiring diagram from leviton for their 14-30R receptacle. It clearly shows a neutral wire being run.

1644866766665.png \
The written instructions say to connect the neutral wire as well.

1644866846313.png
Since this is a listed product, you have to follow the instructions.

As an aside, I have occasionally wondered why you only have to follow the instructions on listed products. :)
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I can understand a little the use of the dryer outlet if one is present. However using the Range outlet. Oh that is a great idea. Trip hazard, CO hazard if a non-EV is running in the garage. I can see it now. Customers drilling hole through wall, passing a rubber cord duct tape to the range terminals......
Yet Telsa only has a 6-50 adapter no 30amp other than the range or Dryer.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Neutral is also required with listed NEMA 14-50R, and our AHJ's enforce that even when used per car charger instructions.
Not using a 14-50 or 14-30. no neutral for a 6-30 or a 6-50... Hence the thread.
 

retirede

Senior Member
Location
Illinois
It seems electric-clothes dryer instructions don't allow the 30A appliance to run on 50A fuses.

If 30A clothes dryer appliance & 50A charger must use the same outlet, a 50A breaker/branch circuit only works if another plug box is used with fuse block for the 30A dryer plug.

See integrated 24 Amp circuit breaker built-in to the transfer switch below.


I wasn’t aware a dryer was part of the scenario. It wasn’t mentioned in the OP.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
I'm a little confused about what you are doing. You want to install a 30 amp breaker feeding a 50 amp receptacle? That is fine but if you are connecting an EV charger with a 50 amp plug it is going to be drawing more than 30 amps.

The standard male plug on EV chargers having a neutral prong (14) is plan stupid and must be sponsored by the copper industry. There is never any connection to the neutral for charging.

I was surprised recently when a neighbor asked me to install a receptacle for their new car. Tesla recommended and sold them a 6-50 adapter for a new circuit.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I'm a little confused about what you are doing. You want to install a 30 amp breaker feeding a 50 amp receptacle? That is fine but if you are connecting an EV charger with a 50 amp plug it is going to be drawing more than 30 amps.

The standard male plug on EV chargers having a neutral prong (14) is plan stupid and must be sponsored by the copper industry. There is never any connection to the neutral for charging.

I was surprised recently when a neighbor asked me to install a receptacle for their new car. Tesla recommended and sold them a 6-50 adapter for a new circuit.
Yes that is the concern. I originally sold the customer on a 6-30 receptacle , then they wanted to have the wire upgraded to plan for the future in case they had a service upgrade as a 50 would be marginal depending on which method you use as a load Cal ( using Mike Holt spreadsheet)
Then the customer says that Telsa does not sell a 6-30 adapter. However a aftermarket does.
Now the plan is to use #8 for the future pull the wasted neutral and charge for it. Install a 14-30 receptacle. How frikin stupid can Tesla and the rest be. This is gonna cost a about 100 bucks for a wire that should not need to be there.
 