The NJ interpretation is wrong. But it makes little sense to worry about it since 6CU SE cable would be allowed and I don't see the difference.
See Pages 13 and 14.
OK, so the problem is bigger than just 210.19(A)(1) and 215.2(A)(1). The problem is that even though the definition of "ampacity" in Article 100 refers to the "conditions of use" and thus to a corrected and adjusted value, many sections like 210.19(A)(1)(a) and 215.2(A)(1)(a) use the term to refer to an unadjusted and uncorrected value straight from the table.FWIW, the NJ result is the correct one on the physics; the error is in the language in 210.19(A)(1) and 215.2(A)(1).