• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

EV Chargers Service Calculation

brycenesbitt

Senior Member
Location
United States
How would you size the service entrance conductors for the OP's proposed four 48A chargers?
I'd leave the SE conductors the same, but install many more charging heads, so the average utilization of the circuit goes up. Four 48A chargers will rarely to never hit their peak all at the same time. So how to size? Start with a given circuit size, then use load management to distribute that to the chargers. Focus on the results first, then see how that affects the upstream SE size.
 
Top