The individual motor branch circuit, the #10 looks big and the 20 amp breaker looks small. Using the old code rules could be #12 with 30 Amp breaker. Did not check it with the new code rules. Feeder looks OK by eye but I might try to go up on the breaker size if I can find a code rule for it, to carry motor locked rotor starting current.
More importantly, the evap fan could be a typical winning drive application. If your rooftop panelboard is outside with no allowance to add drives now or later, I might look it as, well IDK but maybe not useful over the expected useful life.
If the rooftop panelboard is going inside in the rooftop penthouse and you have an allowance for footprint to add drives now or later, I might say that's providing something useful or reuseable when the time comes. I would plan for an inside footprint at the panelboard location where drives can be added in easily.