I have 5 evap coolers. 10hp 460v 3 phase 12.2 amps. FLC is 14 amps. I want to make sure I size my feeder right. We are gonna put a panel board on roof. FLC 14ampsx1.25 =17.5 amps. 4 more motors at 14 amp @ 100%=56 amps. 56x17.5=73.5. Conductor size 4awg cu or 2awg AL. 80 amp breaker. I was gonna put each motor in its own 3/4 emt 10 awg thhn on a 3 pole 20 amp breakers thanks