I'm bidding a job where I plan to replace the main circuit breaker panel.
The existing installation has the grounded (neutral) conductor coming 1) in from the overhead, 2) passing through the meter socket without being connected to anything, and 3) terminating at the neutral bus in the main CB panel.
Then there is a bonding jumper that runs through 1) bonding bushing on the line side of the meter socket, 2) through a bonding bushing on the load side of the meter socket, and 3) to the neutral bus in the main CB panel.
I'm just trying to price the job right. If I have to reroute the neutral to hit the lugs in the meter socket, I'll have to disconnect the overhead and I have to price that in. The service conductors are adequately sized for the load, so there's no independent reason to replace them.
It seems like the existing installation satisfies 250.24(A)(1), but I've always landed the neutral in the meter socket first.
Your thoughts would be appreciated.
Thanks
The existing installation has the grounded (neutral) conductor coming 1) in from the overhead, 2) passing through the meter socket without being connected to anything, and 3) terminating at the neutral bus in the main CB panel.
Then there is a bonding jumper that runs through 1) bonding bushing on the line side of the meter socket, 2) through a bonding bushing on the load side of the meter socket, and 3) to the neutral bus in the main CB panel.
I'm just trying to price the job right. If I have to reroute the neutral to hit the lugs in the meter socket, I'll have to disconnect the overhead and I have to price that in. The service conductors are adequately sized for the load, so there's no independent reason to replace them.
It seems like the existing installation satisfies 250.24(A)(1), but I've always landed the neutral in the meter socket first.
Your thoughts would be appreciated.
Thanks