kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Few things to consider:
1: Wires in free air have a MUCH larger ampacity than in conduit.
2: The demand for multiple occupancies (damn the spell checker, shows me "occupancies" as not a valid word, but MW list it as a valid plural for "occupancy") is MUCH smaller than for one. In fact, 20 some apartments may give you a smaller demand than 3-4 taken at single value.
3: How many fires did you hear about from a POCO perspective? I've heard of a few from the internal wiring.
4: Do you REALLY want POCO to adhere by the NEC rules? I can see our electric bills triple (if not quadruple) if that was the case.
So the question is: "can we make it better?".
Sure, but at what cost?
Keep in mind money is a limited resource.
I know you can't put a price on a life, but here's the deal: do we spend a trillion dollars to save ONE LIFE? while that trillion dollars can save thousands of lives by different methods?
On the lines of what I have been saying throughout this thread - how many lives have been lost due to so called undersized POCO transformers or service drops? Compare that to how many have been lost due to undersized equipment or conductors within a building.
Only problem I run into much with small drops is voltage drop. Ampacity wise you can load them pretty good and they remain intact. Usually voltage drop becomes a big enough issue that something is done about that before it gets to the point of melting down the drop.