M mstrlucky74 Senior Member Location NJ Oct 2, 2018 #1 Is it NEC code to use expansion fittings on conduit at expansion joints even if sepc doesn't call for them?
Is it NEC code to use expansion fittings on conduit at expansion joints even if sepc doesn't call for them?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 2, 2018 #2 Yes.
M mstrlucky74 Senior Member Location NJ Oct 2, 2018 #3 infinity said: Yes. Click to expand... Which section? THink I got 300.7 Last edited: Oct 2, 2018
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 2, 2018 #4 2014 NEC 300.4(H).