don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
But if you have an SDS that transforms to another voltage, there has to be some statement which says the SDS output and associated wiring beyond the disconnecting means is a different system for the purposes of 300.3(C).

I realize we are not going to get anywhere in this debate because of said definition(s) or lack thereof. I just believe it's a noteworthy issue.
You have a valid point, but that is just not how the code is written.

PIs for the 2020 code are due in early November of 2017:)
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The Sola constant vo ltage transformer (CVT) uses a weak coupling between primary and secondary magnetic circuits and then uses a tuned circuit and saturation on the secondary side to limit the voltage there.
Not easy to model or design.
 

n1ist

Senior Member
Location
Massachusetts
Occupation
Principal Electrical Engineer
An MG set is another example of an SDS; we use a 208V 3ph motor to drive a generator for making 50Hz power to test gear going overseas.
 

kwired

Electron manager
Location
NE Nebraska
An MG set is another example of an SDS; we use a 208V 3ph motor to drive a generator for making 50Hz power to test gear going overseas.
If the generator is interconnected to another system it may or may not be separately derived depending on how it is connected. If it's ouput system stands alone it is separately derived.
 

Smart $

Esteemed Member
Location
Ohio
If the generator is interconnected to another system it may or may not be separately derived depending on how it is connected. If it's ouput system stands alone it is separately derived.
The usual determining factor is whether or not the grounded [neutral] conductor is switched by the transfer equipment. If not switched,the genset is not separately derived.
 

kwired

Electron manager
Location
NE Nebraska
The usual determining factor is whether or not the grounded [neutral] conductor is switched by the transfer equipment. If not switched,the genset is not separately derived.
Correct. If not interconnected to another system there is no transfer switch but it is still separately derived source from any other source on the premises. Tie a common conductor of two sources together and they become one system, same with transformers - they become auto transformers other then if all that is tied together is grounded conductors that otherwise don't ordinarily carry current between the two systems.
 