Another option:Dennis Alwon said:Smart I would love to see the file with the .xls. I only have 2003 excel
http://www.microsoft.com/downloads/...70-3AE9-4AEE-8F43-C6BB74CD1466&displaylang=en
However, I will save in older format and post...
Another option:Dennis Alwon said:Smart I would love to see the file with the .xls. I only have 2003 excel
Yeah... but if an exact value in the lookup column is not found an error is returned—#N/A—and "approximate" lookup always uses the row having a value equal to or largest less than the lookup value.energymv said:I use VLOOKUP all the time. The fourth parameter of the VLOOKUP function will determine whether to look for an exact or an approximate match. Use "0" for exact. Use "1" for approximate.
Hmm... that don't work for me.peter said:But I discovered a work around:
What I did was reverse the table so that the highest [800 amps] was at the top of the list and the lowest [15Amp = 15 Amp breaker] was at the bottom. There is a sort button for that [A Z or ZA].
I use Windows Live Space (which actually stores file on SkyDrive) for filetypes you can't upload here or to Photobucket.Dennis Alwon said:No, you have to upload the file to a website.
Yeah the -1 is important!peter said:Smart $,
Sorry about that. I was posting from my laptop which didn't have the Excel program. Now I'm in from my terrace and at my desk and I looked at the program.
It wasn't VLOOKUP after all.
"Breaker size" = INDEX (U8:U36, MATCH (J22,U8:U36,-1))
I'm not sure what all this means since I did it a couple of years ago. But U8:U36 is the inverted list. J22 refers to the input. I dunno what the -1 is but it's probably important.
~Peter
Use a sub-panel!iwire said:For example if I have a roof that has 300 panels, should connect them altogether and run one large 'feeder' back to the inverter or should I break it up into two groups of 150, or maybe 3 groups of 100? :smile:
celtic said:I would suggest www.openoffice.org (O)for those having any issues opening xls type files.
The wave of the future.
LarryFine said:Use a sub-panel!![]()
Actually, regarding Office programs, it had been [fairly] forward compatible until the release of Office 2007.glene77is said:IMHO, The Open Office approach, which is 'Forward Compatible',
is a better approach than MS philosophy,
which is to make things 'Backward Compatible' !!!
Do you derate the wires on the roof as per table 310.15(B)(2)(c)?iwire said:We will be ...... more or less, a lot of them. Only it works in reverse and it's called a combiner box.
The 'branch circuits' are the supply and the 'feeder' is the load.
I have been pretty quiet about the scale of the installation but one area of the roof might require per the NEC 850 amps worth of conductors from the inverter to the combiner box. Or I can use more combiner boxes and more feeders. Once I pass about 300 amps I will have to run parallel feeders anyway so I might as well go the Larry route and opt for two or three combiner boxes spread out to keep the branches short.![]()
tkb said:Do you derate the wires on the roof as per table 310.15(B)(2)(c)?
celtic said:Interesting thought you have there iwire ~ if I find the time, maybe I'll take a stab at it .....
This Excel spreadsheet reads Table 310.16 for copper conductors only. This program is similar to the JavaScript program that reads Table 310.16.