A different issue. If you have a DC motor with a wound field and you loose field excitation, then what happens to the motor speed?
That would depend on how the motor was loaded or what it was coupled to.
I had one a a little over a year ago back where the shunt field had gone open circuit. It was on a Fourdrinier paper (making) machine where speed holding is quite critical.
Well, it carried on running and the machine carried on making paper. The electricians knew there was a problem but production is king and they were not allowed to stop the machine to do any checks.
What happened is that armature voltage dropped to about 100Vdc whereas normal running voltage is close to 600Vdc. It is one of two 300kW motors that are effectively are mechanically coupled in that they both drive the same part of the machine.
There is a load sharing circuit between the two which looks at the current and maintains it in a set ratio. So the motor with the failed shunt field took its correct current, albeit giving much less torque.
Having been told what the symptoms were, I was fairly sure it was an excitation problem but the 100Vdc on the armature got me thinking. The answer in the end was quite simple. It was one of their older motors (c1960) and, as was the practice then, motors for this application had some compounding - there was also a bit of series field resulting the 100Vdc or so back EMF.
In summary, the motor ran that way for about a week until the next planned shut. The fault turned out to be a badly made "temporary" connection in the motor terminal box. From its appearance, it looked like it had been that way for a lot longer than most us would consider to be temporary.