Even though the blower had means of disconnect. Is it still good to use wall switch to control motor starter?use the wall switch to control a motor starter, so you also have overloads
I want the switch to be inside mechanical/lab room.Depends on how and where you want to turn the fan on and off, no?
-Hal
How do I want to turn on/off- toggle switchDepends on how and where you want to turn the fan on and off, no?
-Hal
The wall switch will be a remote control for the starter. You need to determine if there is a power outage should the fan turn on when power is restored. If you don’t want the fan to automatically restart, then you will need to use a start stop push button, so when power drops out, start button is pushed to restart.Even though the blower had means of disconnect. Is it still good to use wall switch to control motor starter?
I want the fan to be on when/if power is restored I case of outage so I want to use switch. Question is the fan is 3 phase, how is single pole work? Isn’t it supposed to be 3 Pole wall switchThe wall switch will be a remote control for the starter. You need to determine if there is a power outage should the fan turn on when power is restored. If you don’t want the fan to automatically restart, then you will need to use a start stop push button, so when power drops out, start button is pushed to restart.
if you use a single pole wall switch, I would use a lighted switch, light on, fan on
Here's a 3 pole switch meant for motors. A few bucks more than a light switch but not much.I want the fan to be on when/if power is restored I case of outage so I want to use switch. Question is the fan is 3 phase, how is single pole work? Isn’t it supposed to be 3 Pole wall switch
Thank you.Here's a 3 pole switch meant for motors. A few bucks more than a light switch but not much.
Sent from my SM-G965U using Tapatalk
Basically what I have from my understanding 430.102.The switch will work, but you will need to provide overload protection for the motor and a disconnect within sight of the motor. If the switch is considered the controller you will need a disconnect for it.
suggest you review section 430.102
I think there are some small 3 phase motors that have built in overload protection.No, you can't use that.
3 phase motors have no overload protection so you have to provide a motor starter that will provide overload protection. The starter has a contactor that you can control with a single pole toggle switch to turn the fan on and off. You will also need to supply a disconnect switch in most instances between the panel and starter.
-Hal
Yes there are motor starter built in with overload protectionI think there are some small 3 phase motors that have built in overload protection.
What I am thinking is the disconnect switch, and motor starter(controller) is within sight of the motor.
And the toggle switch will not be within sight.
Would this change if the motor was single phase?