hillbilly said:Brady Electric said:"I have hung chandlers above tubs before but you could not reach it from the tub and on a GFCI circuit. Semper Fi.Buddy"
If that chantileer was cord connected and hanging on a chain, cord or cable, it wasn't code compliant. 410.4(D) 2005
steve
If the chandelier were 8' above the tubs' edge wouldn't it be compliant? He said that the fixture was out of reach.
infinity said:If the chandelier were 8' above the tubs' edge wouldn't it be compliant? He said that the fixture was out of reach.
charlie b said:Just out of curiosity, where is the rule that says you cannot install anything unless it is listed? I know where to find the rule that says, IF it is listed, THEN you must install and use it in accordance with the instructions that came with the listing. But what if it is not listed?
tallgirl said:410.4 (D) -- "Luminaires (lighting fixtures) located in this zone shall be listed for damp locations"
charlie b said:Just out of curiosity, where is the rule that says you cannot install anything unless it is listed? I know where to find the rule that says, IF it is listed, THEN you must install and use it in accordance with the instructions that came with the listing. But what if it is not listed?
In this example, suppose you ask the HO to prove the item is listed for the wet (or damp or whatever) environment. Suppose the HO says that he built the fan himself, out of used pin ball machine parts? What rule would you use to fail the installation? Is there such a rule in the NEC, or would you have to look into building codes?
tallgirl said:Define "out of reach". I can touch an 8' ceiling flat-footed. My kid brother can place his palm flat on an 8' ceiling flat-footed. What would be "out of reach" for me isn't for him.
I don't see how a chandelier -- and especially a chandelier -- mounted over a tub can be done in a compliant manner. I've never seen a chandelier rated for a damp or wet location (could exist, I suppose ...), and unless the ceiling is high enough so that all of the chandelier is above 8', this sounds like a 410.4 (D) no-no.
infinity said:hillbilly said:If the chandelier were 8' above the tubs' edge wouldn't it be compliant? He said that the fixture was out of reach.
The problem is not the 8' above the bathtub's rim, it's the 3' horizontal from the bathtub's rim that governs the placement of the fixtures that I mentioned. They can't go directly over the bathtub regardless of how high they are, even if they're rated for wet/damp location.
hillbilly said:The problem is not the 8' above the bathtub's rim, it's the 3' horizontal from the bathtub's rim that governs the placement of the fixtures that I mentioned. They can't go directly over the bathtub regardless of how high they are, even if they're rated for wet/damp location.
What code section do you have to back that up? I'd say that any fixture can go over a bathtub if it's out of the tub zone. The tub zone is 3' from the edge and 8' above the rim.
Jim W in Tampa said:Dang you aint kidding about your name are you .
infinity said:hillbilly said:What code section do you have to back that up? I'd say that any fixture can go over a bathtub if it's out of the tub zone. The tub zone is 3' from the edge and 8' above the rim.
410.4(D) (2005) Bathtub and Shower Areas. No parts of cord connected luminaries (fixtures) , chain-, cable, or cord suspended luminaries (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900mm (3 ft.) horizontally AND 2.5m (8 ft.) vertically from the top of the bathtub rim or shower threshhold.
This zone is all encompassing and includes the zone directly over the tub or shower stall.
Lumunaries (lighting fixtures) located in this zone (Those that are allowed...my words) shall be listed for damp locations, or listed for wet locations where subject to shower spray.
The type that I listed can't be directly over the tub or shower, anywhere in the zone.
That's the way that I read and understand it.
steve
hillbilly said:410.4(D) (2005) Bathtub and Shower Areas. No parts of cord connected luminaries (fixtures) , chain-, cable, or cord suspended luminaries (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900mm (3 ft.) horizontally AND 2.5m (8 ft.) vertically from the top of the bathtub rim or shower threshhold.
This zone is all encompassing and includes the zone directly over the tub or shower stall.
Lumunaries (lighting fixtures) located in this zone (Those that are allowed...my words) shall be listed for damp locations, or listed for wet locations where subject to shower spray.
The type that I listed can't be directly over the tub or shower, anywhere in the zone.
That's the way that I read and understand it.
steve
tallgirl said:"Right, but what I read the other poster as saying is that once you're more than 8' above the tub rim or shower threshhold, you're outside that zone -- same as if you were more than 3' horizontally from the tub or shower -- and anything goes".
"The zone is a bounded box -- it doesn't extend indefinitely into outer space ..."
410.4(D) Doesn't say 3 ft. horizontally....OR....8 ft. vertically.
It says 3 ft. horizontally....AND....8 ft. vertically. It has to be both.
You're right, it's like a box. My opinion is that the closest point of the (referenced) fixtures has to be mounted at the upper and outer corner of the box (minimum). You can't disregard one dimension just because you meet the other.
In my opinion...You can hang it as high as you want over 8 ft., but if it's not at least 3 ft. horizontally from the edge, it's not code compliant.
That's what I understand it to say.
hillbilly said:but if it's not at least 3 ft. horizontally from the edge, it's not code compliant.
That's what I understand it to say.
infinity said:If the zone is a box than if the fixture is above the zone or adjacent to the zone it's not in the zone. Any fixture can go outside of the zone. Be it 3' from the edge or more than 8' above the rim.