We have a client that complains about an exhaust fan motor that keeps "Burning Up" because of high ambient temp. It is in a gas compressor building above a large internal combustion engine. And yeah, it gets pretty toasty in there. I've reached out to a supplier, but wanted you fine folks' ideas, too.
The motor is a Baldor, 230V, single phase, 184T frame, 2 HP, 1750 RPM, Class B insulation, capacitor start, explosion proof. Don't know what sort of controller, yet. Might just be a breaker. I got looking on line for one with a higher insulation class, but can't find much. Seems there are few choices in single phase.
Sooo .... am looking for options if a single phase motor with a higher insulation class is not available. What do you guys think of:
Upping the motor/controller to 3 HP that would generate less heat
Installing a VFD so that a 3-ph motor with a higher insulation class can be used
Other options?
The motor is a Baldor, 230V, single phase, 184T frame, 2 HP, 1750 RPM, Class B insulation, capacitor start, explosion proof. Don't know what sort of controller, yet. Might just be a breaker. I got looking on line for one with a higher insulation class, but can't find much. Seems there are few choices in single phase.