To me as far as the paralled switch loops, I dont think this is what the code panel
had in mind when they made this code.They where trying to limit the use of smaller conductors for feeds if it wheren't for this code instead of running 6/3 to the rangea lot of contractors would probably parallel 3 # 10/3 nm cables what a mess this could be.
Ronals
I dont think this is what the code panel
had in mind when they made this code.
I have this exact same scenario for 4 bathrooms and one ex. fan for a warehouse. Four single pole switches on switch loops driving a contactor is what I'm going with. Occ. sensors would be ideal, but not if they weren't bid....
Technically speaking, when more than one switch is on, you still have paralleled conductors. The only difference is the load is a coil instead of the fan.Four single pole switches on switch loops driving a contactor is what I'm going with. Occ. sensors would be ideal, but not if they weren't bid....
310.4(A) General. Aluminum, copper-clad aluminum, or copper
conductors of size 1/0 AWG and larger, comprising each
phase, polarity, neutral, or grounded circuit conductor shall
be permitted to be connected in parallel (electrically joined
at both ends).
Technically speaking, when more than one switch is on, you still have paralleled conductors. The only difference is the load is a coil instead of the fan.
I don't have a problem with paralleled switching. I just mentioned it because others have.