Exhaust Fan...

Status
Not open for further replies.

chevyx92

Senior Member
Location
VA BCH, VA
Manufactured rooftop exhaust fan for small kitchen hood has a prewired disconnect switch that has the hot and neutral on the switch. I'm suppose to supply 120v to this switch. The switch is a double pole double throw. Is this legal? Why is the neutral on the switch? Is there something that allows this?
 
Last edited:
It is legal and quite common on HVAC equipment. Typically fan power boxes have a small double pole toggle switch with the exact same setup. Can't say that I know why.
 
chevyx92 said:
Does 430.105 justify this setup?


I don't know if justify is the right word. I would say that 430.105 definitely permits this installation but doesn't shed any light as to why the manufacturer has it set up this way.
 
infinity said:
I don't know if justify is the right word. I would say that 430.105 definitely permits this installation but doesn't shed any light as to why the manufacturer has it set up this way.
I guess thats what I was looking for. An article that allowed this setup.
 