Exhibit 210.26 commentary

Status
Not open for further replies.

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
In reading the commentary on PP 100 of the handbook it says "Where additional small-appliance branch circuits are installed, they are subject to all the requirements that apply to the minimum two required circuits."

So does this mean the a circuit for a disposal or a DW must be on a 20 AMP circuit?
Have I been in violation by installing a 15 AMP circuit(s) for these?

I know it is the commentary. Just tell me how you read it.
 

Hendrix

Senior Member
Location
New England
In reading the commentary on PP 100 of the handbook it says "Where additional small-appliance branch circuits are installed, they are subject to all the requirements that apply to the minimum two required circuits."

So does this mean the a circuit for a disposal or a DW must be on a 20 AMP circuit?
Have I been in violation by installing a 15 AMP circuit(s) for these?

I know it is the commentary. Just tell me how you read it.
I believe that is for countertops only. Although I may be wrong. :confused:
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
SABCs are for wall, floor, countertop, and refrigeration receptacles. The receptacles under the counter that serve the dishwasher and the disposal are not covered by this section. They can be 15 amp.
 

elohr46

Senior Member
Location
square one
Good question. I believe it only applies to small appliance circuits and not fixed appliances fastened in place. When I read the last paragraph in exhibit 210.26 I come to that conclusion.
 
Status
Not open for further replies.
Top