Existing Grounding electrode system

Status
Not open for further replies.

alixenos

Member
Location
Florida
Occupation
Electrical Design Engineer
Hi,

an electrical room that has an existing 1200A main switchboard is updated to have another 1200 A main switchboard being served from a new service.

for the 2nd service, Do we need to provide a new grounding electrode system? what about the existing one? where in the code I can find answers to those questions?

Thank you.
 
The new service has to be connected to a GES. If there is an existing GES you can use it. There is no requirement to install a new GES when adding a service to a building that already has one.
 
I would add that you will most likely need to connect to the existing system on the new service.

250.50 - "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system."

250.58 - "... If separate services, feeders, or branch circuits supply a building and are required to be connected to a grounding electrode(s), the same grounding electrode(s) shall be used."
 
I would add that you will most likely need to connect to the existing system on the new service.

250.50 - "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system."

250.58 - "... If separate services, feeders, or branch circuits supply a building and are required to be connected to a grounding electrode(s), the same grounding electrode(s) shall be used."
And if someone decided to install a new electrodes or a new GES they would have to be connected to the existing GES.
 