Hi! First post, so go easy on me.
I've got an Eaton CH404040SH where the secondary main circuit breaker feeds an MLO Eaton BR-type subpanel. There is 21kA of available fault current from the utility. My understanding is that the BR-type branch breakers in the subpanel are series rated to 25kaic with the CSR-type main circuit breaker in the SES, even though that main breaker is in a separate enclosure.
Now the slightly more complicated part - we're asked to install a solar and battery system, using the existing MLO subpanel as the backed up loads panel. So a bunch of equipment gets added between the CSR main breaker in the SES and the BR branch breakers in the MLO subpanel (a fused disconnect, an unfused disconnect, and the Tesla Backup Gateway). Does the series rating still apply? Or do we have to replace the MLO subpanel with a panel that has a main circuit breaker?
I've got an Eaton CH404040SH where the secondary main circuit breaker feeds an MLO Eaton BR-type subpanel. There is 21kA of available fault current from the utility. My understanding is that the BR-type branch breakers in the subpanel are series rated to 25kaic with the CSR-type main circuit breaker in the SES, even though that main breaker is in a separate enclosure.
Now the slightly more complicated part - we're asked to install a solar and battery system, using the existing MLO subpanel as the backed up loads panel. So a bunch of equipment gets added between the CSR main breaker in the SES and the BR branch breakers in the MLO subpanel (a fused disconnect, an unfused disconnect, and the Tesla Backup Gateway). Does the series rating still apply? Or do we have to replace the MLO subpanel with a panel that has a main circuit breaker?