Existing fuel station is reconfiguring outside fuel canopy and tanks. The new tanks and lines will cross existing service feeder to store. Would the service need to have seal offs at each end? What other issues do you see with a project like this? Or maybe there isnt one.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Will the classification documentation be updated? [500.4] If so, any underground must be installed consistent with Section 514.8; i.e., if the service is run beneath or through classified locations, it will need to be sealed where it emerges from grade.
 