It says more than two cables. You could conceivably have two-four wire cables and 8 CCC's and still not require derating.
You still have to derate with 8 CCC's, just so happens that normally the result of the deration doesn't require an increase in conductor size - especially when derating a 60 deg termination application while using 90 deg insulation conductors.
I should have been more clear, I was commenting on 334.80 where no derating is required for two cables regardless of the number of CCC's.