There are expansion joint fittings available for EMT. I can find reference to expansion joints in 300.7 (B), which requires them "where necessary", a rather vague requirement.
1. Would an expansion fitting always be required at a building expansion joint, considering that some "give" would be expected with a normal EMT installation? Especially if the run is short?
2. Here is a calculation of expansion in 10 feet of EMT over a typical temperature range in my state:
Expansion coefficient of steel 6.50E-06 in/in/?F per NEC 300.7 (B) FPN
for 10 feet of conduit: 120 inches
6 F design temperature winter
99 F design temp summer
not subject to direct sunlight
93 delta T, ?F
0.072" expansion in 10 feet of conduit due to temperature change.
I would argue that .07" of expansion is negligible, and expansion joints are not needed in runs of EMT under 10 feet.
Any opinions?
1. Would an expansion fitting always be required at a building expansion joint, considering that some "give" would be expected with a normal EMT installation? Especially if the run is short?
2. Here is a calculation of expansion in 10 feet of EMT over a typical temperature range in my state:
Expansion coefficient of steel 6.50E-06 in/in/?F per NEC 300.7 (B) FPN
for 10 feet of conduit: 120 inches
6 F design temperature winter
99 F design temp summer
not subject to direct sunlight
93 delta T, ?F
0.072" expansion in 10 feet of conduit due to temperature change.
I would argue that .07" of expansion is negligible, and expansion joints are not needed in runs of EMT under 10 feet.
Any opinions?