AFCI testing data
AFCI testing data
I finally got some time to start testing my QO115CAFIC. My ultimate goal is to better understand just what the test switch accomplishes. In the partial schematic I have seen it appears only as an input to the microcontroller.
Without knowing what the firmware does this leaves it open to being as simple as tripping the latch?
I hope to better understand what the test switch does later.
In working up to that I have tested several loads such as 3 different vacuum cleaners and 900 watt heater loads. The heater loads were in series with a cheap phase fire type dimmer set at 25%, 50%, 75% and 100% setting and the breaker held fine (no nuisance trips).
This was in an attempt to create a load that might "simulate a series arc" so that I can develop a repeatable test I know will trip the breaker when seen as an arc. This is was also to identify what kinds of loads would not false trip the breaker.
I further tested to confirm the GF leakage trip point of the device at ~40ma. It held at 38 ma for more than 10 seconds and tripped at 42 ma in less than 2 seconds.
It held with a 4 watt night light as a load (hot to ground) even though the cold resistance measured about 300 ohms. Hot current = 33 ma
Thus far the most interesting was its detection of a Neutral to Ground connection. The breaker tripped with a direct short between load Neu. and Ground just fine. I was surprised to see that it held with anything greater than ~0.2 ohms. So this appears to indicate that a pretty good connection (neu-gnd) is required downstream of this to appear as this type of fault.
Manually tripped the test switch and the only current recorded on the input hot line was a 3 amp 1/2 cycle pulse required to power the coil to trip the unit.
I will now work towards creating my repeatable arc fault. I considered using carbon rods in series with my heater load but that seemed a but messy. I am considering building a electronic "arc simulator" where I can control the waveforms shape.
I know some "Arc Fault Testers" are sold out there but I have not seen one that gave thorough specifications on its capabilites so I am leary of investing in one. Then again I am not sure I have the time and energy to build my own either. Could be fun Suggestions on possible (electronic) arc type loads welcome
AFCI testing data
I finally got some time to start testing my QO115CAFIC. My ultimate goal is to better understand just what the test switch accomplishes. In the partial schematic I have seen it appears only as an input to the microcontroller.
Without knowing what the firmware does this leaves it open to being as simple as tripping the latch?
I hope to better understand what the test switch does later.
In working up to that I have tested several loads such as 3 different vacuum cleaners and 900 watt heater loads. The heater loads were in series with a cheap phase fire type dimmer set at 25%, 50%, 75% and 100% setting and the breaker held fine (no nuisance trips).
This was in an attempt to create a load that might "simulate a series arc" so that I can develop a repeatable test I know will trip the breaker when seen as an arc. This is was also to identify what kinds of loads would not false trip the breaker.
I further tested to confirm the GF leakage trip point of the device at ~40ma. It held at 38 ma for more than 10 seconds and tripped at 42 ma in less than 2 seconds.
It held with a 4 watt night light as a load (hot to ground) even though the cold resistance measured about 300 ohms. Hot current = 33 ma
Thus far the most interesting was its detection of a Neutral to Ground connection. The breaker tripped with a direct short between load Neu. and Ground just fine. I was surprised to see that it held with anything greater than ~0.2 ohms. So this appears to indicate that a pretty good connection (neu-gnd) is required downstream of this to appear as this type of fault.
Manually tripped the test switch and the only current recorded on the input hot line was a 3 amp 1/2 cycle pulse required to power the coil to trip the unit.
I will now work towards creating my repeatable arc fault. I considered using carbon rods in series with my heater load but that seemed a but messy. I am considering building a electronic "arc simulator" where I can control the waveforms shape.
I know some "Arc Fault Testers" are sold out there but I have not seen one that gave thorough specifications on its capabilites so I am leary of investing in one. Then again I am not sure I have the time and energy to build my own either. Could be fun Suggestions on possible (electronic) arc type loads welcome