6.1.2 Control of electronic logic circuits. Contact bounce and transfer time of most sensitive, snap action basic switches is of concern when used to control devices having very fast response time. In the
case of a double throw, break-before-make, snap action switch, there is no circuit through either contact during the transfer (snap over) time. Thus, there will be a definite interval between the time one circuit opens and the other closes. Associated with circuit closure is contact bounce. When the moving contact strikes the stationary contact, the kinetic energy is converted to heat and potential energy in the form of deformation of the contacts. As a result of elastic deformation, the moving contact rebounds from the stationary contact, the contact pair being reclosed by the contact force. This can occur one or more times until bouncing ceases and the contact system reaches static equilibrium. In general, the combined transfer time and bounce time will usually not exceed five milliseconds and cause no problems on slow responding devices. On fast responding electronic logic circuits, each contact bounce may be erroneously interpreted by the circuit as a separate signal causing a false output. To compensate for the contact bounce of the switch, a ten millisecond buffering circuit is usually adequate to
prevent false outputs of the logic circuit.
The environmental conditions in which a switch must control a logic load level or low level electrical load may directly affect its performance in the application. Under these electrical load conditions, there is no arc present to remove contamination from the contact interfaces which prevent proper contact closure.
The probability of proper contact closure under nonarcing conditions is inversely proportional to the contamination in the environment. The detrimental effects of environmental contamination can be significantly reduced by one or more of the following:
a) Enclosure: By enclosing the contacts in a sealed enclosure, the contacts are protected from the environment.
b) Contact material: The use of gold at the contact interface will prevent the formation of sulfides and oxides.
c) Contact configuration: There are two basic contact concepts specifically suited for nonarcing electrical loads:
(1) Multiple-point contact designs to provide redundancy such as bifurcated contacts.
(2) Point-to-plane or point-to-point contact designs such as wedge-shaped contacts, crossed-cylinder contacts, or crossed-prism contacts.