I have junction boxes that will be located in a class 1 div 2 area. If all that will be in these junction boxes are terminal strips, is a explosion proof panel and conduit seals still required in the hazardous area?
Boxes and Fittings. Boxes and fittings shall not be required to be explosionproof except as required by 501.105(B)(1), 501.115(B)(1), and 501.150(B)(1).
Section 501.10(B)(4):
Basically, if the contents aren't arcing, sparking, or high temperature (ASH) under design conditions, the enclosure isn't required to be explosionproof. Of course, it must still be suitable for the environment.
rb, you consider boxes and fittings to include enclosures/junction boxes, conduit fittings, and cable glands correct?