What part of an LBY25 condulet is an arc producing device?


JAP>
 
Ok. So the seal offs are only required when there is an arc producing device? Sorry, don't do a lot of classified location work.

Not only for arc producing devices in Class I Div 2, but also for boundary changes for one classification to another
Also note, Class I, Division 1 conduit/cable sealing applications are far more stringent.


Sent from my iPhone using Tapatalk
 
Agreed.

Which makes an install interesting at times seeing as how there are very few fittings that are allowed between the seal and the penetration of the boundary.

JAP>
 
Agreed.

Which makes an install interesting at times seeing as how there are very few fittings that are allowed between the seal and the penetration of the boundary.

JAP>

Right, the fewer the better - it must be within 10 feet of boundary


Sent from my iPhone using Tapatalk
 