what article states that energized wires that are exposed must be wrapped in tape or be placed in wire nuts and enclosed in a juction box with cover.these are often when replacing old wiring.
300.15 Boxes, Conduit Bodies, or Fittings ?Where Required.
A box shall be installed at each outlet and switch
point for concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific
wiring methods for which they are designed and listed.
Where the wiring method is conduit, tubing, Type AC
cable, Type MC cable, Type MI cable, nonmetallic-sheathed
cable, or other cables, a box or conduit body shall be installed
at each conductor splice point, outlet point, switch point, junction
point, termination point, or pull point, unless otherwise
permitted in 300.15(A) through (L).
110.14B
"All splices and joints and the free ends of the conductors shall be covered..."
110.14B
So if I tape them I am good to go.
You think that "free ends" only refers to parts of a splice and free (unterminated) ends of wires?
I do not read it that way unless there is "scope' that makes that clear.
(B) Splices.