mkgrady
Senior Member
- Location
- Massachusetts
I'm installing a whole house standby generator on a residence. The ATS will now become the service disconnect and the existing main breaker panel will become a sub panel. I will need a longer SE cable from the meter to the ATS than what is existing. The existing panel is in the basement just below the outside meter.
On this job it will be difficult to replace the SE cable (underground service entrance) so I'm planning to extend it a couple of feet with a splice and a junction box. I have never extended an SE cable before and I'm wondering what my options are. The simplest way seems to be to use a PVC junction box and SE cable connectors to attach the cables to the box. I won't have to ground the box. I have no idea how to ground the metal connectors but it's hard to imagine how they would become energized.
My first thought was to use a metal box but then I thought about how the box would get grounded. Obviously there isn't an equipment ground in the SE cable and connecting a metal box to the neutral seems wrong anywhere but the main disconnect.
As an alternative, what would be wrong with splicing onto the SE cable conductors within the existing main breaker service panel. They could be made long enough to run through a short nipple and terminate at the ATS and then run back through the same nipple from the load terminals of the ATS.
Any code violations in either plan?
On this job it will be difficult to replace the SE cable (underground service entrance) so I'm planning to extend it a couple of feet with a splice and a junction box. I have never extended an SE cable before and I'm wondering what my options are. The simplest way seems to be to use a PVC junction box and SE cable connectors to attach the cables to the box. I won't have to ground the box. I have no idea how to ground the metal connectors but it's hard to imagine how they would become energized.
My first thought was to use a metal box but then I thought about how the box would get grounded. Obviously there isn't an equipment ground in the SE cable and connecting a metal box to the neutral seems wrong anywhere but the main disconnect.
As an alternative, what would be wrong with splicing onto the SE cable conductors within the existing main breaker service panel. They could be made long enough to run through a short nipple and terminate at the ATS and then run back through the same nipple from the load terminals of the ATS.
Any code violations in either plan?