Extension cord use

Status
Not open for further replies.

SmithBuilt

Senior Member
Location
Foothills of NC
The fire marshal has written a couple of violations for my church. Is an extension cord used to power an organ for a church a violation? Or for a desktop lamp?

The organ is hardly portable. Would you consider that a substitute for permanent wiring?

They will allow us to leave it if we install a surge protector with a built in breaker.
 
I would think that, yes, it is being used as a substitute for a permanent wiring method. Every organ I have seen in a church wasn't easily movable.
 
Yes, they write them up all the time around here too. I remember reading the code citation once. It might have come from the building code. Extension cords are only for temporary use, and temporary has a definition; no more than 90 days.
 
400.8.
wink1.gif
 
Offer your services to correct the problem. Ask for a letter from the church so you can deduct your bill from your taxes.
 
There are several manufacturers of list plug strips with 15 ft cords, the ones I like and our fire dept likes are SL Waber, no TVSS and a metal case.
The 15 ft cord is a great bonus.
 
Or just unplug the thing when you are done each Sunday. Temp and less then 90 days. Although it would not take much to add a receptacle or move the organ.
 
I thought the NEC stopped at the receptacle in this particular situation? Seems like you might as well outlaw power strips behind every homes entertainment center if that's the case.
 
I see article 640.3(E) Assembly Occupancies ,refering it to article 518, 518.4(A)ex(a) sends

it back to 640, 640.9 Wiring Methods > 640.9(A)(1) shall comply with Chapter 1-4.

IMO, no extention cords for this peice of equipment in this place of assembly.
 
Last edited:
I thought the NEC stopped at the receptacle in this particular situation? Seems like you might as well outlaw power strips behind every homes entertainment center if that's the case.


2008 UL White Book said:
Relocatable power taps are not intended to be permanently secured to
building structures, tables, work benches or similar structures, nor are they
intended to be used as a substitute for fixed wiring. The cords of relocatable
power taps are not intended to be routed through walls, windows, ceilings,
floors or similar openings.
I would think that the use of one of these to protect the extension cord is a violation of it's listing.
 
The fire marshal has written a couple of violations for my church. Is an extension cord used to power an organ for a church a violation? Or for a desktop lamp?

The organ is hardly portable. Would you consider that a substitute for permanent wiring?

They will allow us to leave it if we install a surge protector with a built in breaker.
Most places the FM have rules against using extension cords.

Its mostly a good thing.

Not necessarily a NEC issue though.
 
Yes, they write them up all the time around here too. I remember reading the code citation once. It might have come from the building code. Extension cords are only for temporary use, and temporary has a definition; no more than 90 days.

I thought 590.3 (B) had it - but that 90 day restriction is for holiday lighting & such...

IMO Extension cords are considered temporary.
 
Is this job under construction I almost get the feeling that this is a finished building. If so how long has the co been in place? Is there any leg for this inspector to enforce these changes if this job has been issued a co? Was the co given with items to be added or changed?
 
Is this job under construction I almost get the feeling that this is a finished building. If so how long has the co been in place? Is there any leg for this inspector to enforce these changes if this job has been issued a co? Was the co given with items to be added or changed?

Did you even read through the whole thread ?
 
Is this job under construction I almost get the feeling that this is a finished building. If so how long has the co been in place? Is there any leg for this inspector to enforce these changes if this job has been issued a co? Was the co given with items to be added or changed?

Did you even read through the whole thread ?

My apology's to Billdozier, my responce was a bit rude and uncalled for, Sorry Bud.
 
In the 2007 CFC...CH6 section 605.5 covers their use and 605.5.1 covers the plugging in to a power tap. Someone in another state can get say what the IFC has to say...

edit to add: 605.5--->extension cords as permanent wiring. 605.5.1----->Extension cords plugged in to power strips.
 