Re: Exterior breaker panel installation
Ampacity adjustment as per 310.15(B)(2)(a) is required, and it is not occupancy specific.
BUT... for small conductors such as 14, and 12 AWG it is not as big a concern because you are permitted to use the 90 degree column to start your calculations - which in most cases, after adjustment, will not drop the ampacity below 15 amps(14 wire) or 20 amps(12 wire).
[ March 06, 2005, 07:56 AM: Message edited by: pierre ]
Ampacity adjustment as per 310.15(B)(2)(a) is required, and it is not occupancy specific.
BUT... for small conductors such as 14, and 12 AWG it is not as big a concern because you are permitted to use the 90 degree column to start your calculations - which in most cases, after adjustment, will not drop the ampacity below 15 amps(14 wire) or 20 amps(12 wire).