exterior lighting

Status
Not open for further replies.
I am running a branch circuit from the main panel underground to an exterior breaker panel with breakers. 60 amp breaker inside to a exterior panel then from exterior breaker box to gate motors and lighting. USE CABLE water resistant , mold resistant, perfect for application. Question XHHW has almost the same qualities can you do direct burial on branch circuit with out complications and still stay with in the code. state is michigan.
 
USE can be used as a branch circuit. XHHW is good for wet location but not direct burial thus it may be used in a raceway.

338.10(b) Exterior Installations. In addition to the provisions of this article, service-entrance cable used for feeders or branch circuits, where installed as exterior wiring, shall be installed in accordance with Part I of Article 225. The cable shall be supported in accordance with 334.30. Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340.
 
What about just using type UF cable?
Is the temperature factor an issue?
For whatever the reason, I know it used to be available as single conductor. It was supplied to us by our distributor for connecting that European low-density radiant heating film crap that was so very popular many years ago.
 
KJay said:
What about just using type UF cable?
Is the temperature factor an issue?
For whatever the reason, I know it used to be available as single conductor. It was supplied to us by our distributor for connecting that European low-density radiant heating film crap that was so very popular many years ago.
I would like to {thank you} most of my experience is in industial wiring, residential has a little more of a twist. I keep reading and like to get other peoples opinons as every day I am still learning. Again thank you soo much!
 