Re: Exterior packaged hot tub
Hi JW,
The tub cannot be bonded to the grid, it is wood and foam. The tub motor will have an equipment ground on it, so adding a grid under the tub embedded in the thinset (typically only about an 1/8 to 1/4" thick, they would have to modify the setting for a grid to fit, I guess)then landed on the....motor (I see that in an earlier post)? How is it the tile can have a potential relative to the water? I can see it in pools and other at or below grade items.
We are bonding the tub to the grid, we are not grounding the grid to the earth as is implied by the earth contact
When you posted landing this grid on the motor and the motor must have an equipment ground, then in essence I would be bonding the grid to ground via the equipment ground path back to the service.
If the finish floor is ceramic tile then you will need to install an equipotential bonding grid as outlined in 680.26 (C)(3). This grid will bond to the pump motor with a #8.
Honest JW, If I can clearly see the "potential" (tongue in cheek) for a potential between tile having no connection to ground or any electrical source and the water that may have connection to an electrical source if a problem develops, to exist in this case, I will go to the City and ask for their understanding. I will just have to hope they do not tell the GC I went behind his back. I believe if I approached the GC he will say NO WAY and then I would be forced to go to the City because this would then be a life safety issue and he would know I did. I do a LOT of work for this GC.
gary
[ August 06, 2005, 10:14 PM: Message edited by: grasfulls ]