I posted previously regarding the use of single lamp remote heads and Article 700.16. I gave an example of using a single remote head in a restroom, but I really needed help with the use of a remote head with 1 lamp on the the exterior. I typically show a single lamp remote head (Surelite 6X9WWH) powered from a Surelite LPXH exit sign at the exterior side of each door marked as an exit. For the second time in literally 6 years of receiving plan review letters for hundreds of designs, I have had single lamp remote heads rejected because of 700.16 stating that any "space" can not be left dark if a lamp burns out. I'm not debating whether or not remote heads are required at the exterior sides of egress doors, I'm not a building official but they say they want them so we show them - everything's good there. NEC doesn't define "space" so I'm unable to determine if "space" refers to the area outside an exit door.
Am I (and many many other plan reviewers) incorrect or is this 1 plan reviewer from a certain city in which I've done 2 jobs in the past 6 years incorrect. Twin remote heads causes a big problem in designs because the high output battery packs in most exits will run (3) em lamps, which is normally the 2 on the exit fixture and the 1 outside the door. I'm aware I can add em lights with no heads, UL 924 listed emergency light fixtures, etc. but we design only retail which is very cost sensitive right now.