Mavtech
 - New Stanton, Pa.
A lot of our products are shipped out of the Continental United States which results in a multitude of codes that must be adhered to, generating a lot of debate over what is proper and what is not as it applies to all the code requirements.  One major topic that is constantly being reviewed is the use of flexible conduit sections to connect between rigid conduit and rotating/vibrating equipment.  We have been using the flexible conduit connectors with the external grounding connection, but the one consistent argument that always come to head is what size conductor we are to use for the ground connection.  These conduit runs are all instrumentation control, there is no power or voltage above 24 VDC.  One group says that since the instrument control HART system is using 16 AWG stranded, then the ground connection should match this size, the other group states that if you do not match the current carrying capability of the internal metal core of the flexible conduit, then you a derating the parallel ground, basing this last argument on the OEM's data that 1/2" flex metal core is approximately the same as #12, 3/4" flex metal core is approximately the same as #10 in regards to the current carrying capability of the inner metal core.  Most of this external flexible conduit grounding is for our CSA customers, but it is becoming very popular and we would like to standardize as much as possible.  Any help, direction, or suggestions would greatly be appreciated.