If a transformer pad, external to the main building, has its own grounding grid (ground rods + 4/0 welded loop), is it code compliant? Does it need to tie into the main building electrode?
IMO, it is compliant as is.If a transformer pad, external to the main building, has its own grounding grid (ground rods + 4/0 welded loop), is it code compliant? Does it need to tie into the main building electrode?
Determine as you will, but I see this as a gray area, subject to the interpretation powers that be. For example, even though outside the building, some will say compliance with 250.30(A)(4) is still required. There is nothing in the Code that says the GEC is not required if the transformer is outside the building. The other side of the fence is lined with people that say the transformer is a separate structure, so 250.30(A)(4) Exception No. 1 applies....
I am trying to determine if the original grounding grid for the external transformer, that was on the drawings, was efficient and code compliant. ...