......Why fill the box with all those jumpers and on a 4 gang you will have 5 conductors to wire nut together.
When I get into 4- and 5-gang boxes, there's more than one circuit in 'em. So a tons of jumpers under one wire nut is a non-issue.
......Why fill the box with all those jumpers and on a 4 gang you will have 5 conductors to wire nut together.
Here's a 3-gang showing how I leave it when I'm done at rough:
![]()
I see now what you meant , I thought you meant the two wires for each switch was a cable coming into box where each switch was located , I see now you place the two wires or three in the correct spot . Yea no brainer to wire , if I left mine for some one else they would have to know what to do with the common loop wire . My previous post wont make much sence because I misunderstood what you meant![]()
More than a 1/4" of sheathing in the box. Some here would fail you. LOL.
It is a terminal. Not rated for feed through. Read 110.14(A).
I dont follow , there is no difference except instead of a hot jumper ran to each switch and wire nut to hot in , the same hot in just loops to each switch. why would some one else go back and cut it off with switches in ? If it is cut off before then I wire it your way . A 3 way gets a hot the same way , and the two travelers on the other screws to the 14 /3 with neutral , dont they know where the 3 way goes , no matter if the hot is long or short :-?
It is a terminal. Not rated for feed through. Read 110.14(A).
I go more by the box type and device going in . If I leave 3 " past the front of outlet box , it was a mistake and there is no more slack to pull . I will leave 4 to 6 on a single gang , I try to eyeball 5 " . I know any more will just get sniped off , so not have to pack it in device box. Now multi gang is another thing I will leave 8 or more , somtimes I loop the hot and grounds around the screw terminals from first switch to the last in box. of course each switch has its on hot leaving the box to fixture . and the neutrals nut together. Does anyone know if it is a violation to loop between switches that way.![]()
It is a terminal. Not rated for feed through. Read 110.14(A).
How many conductors are under that screw? Just one - it's compliant.
I agree with George.
When I get into 4- and 5-gang boxes, there's more than one circuit in 'em. So a tons of jumpers under one wire nut is a non-issue.
Im surprised more here dont loop on conduit and stranded wire its a lot easier to get the stranded to stay under the screw when you have a loop to pull tight when the screw is tightened and the strand wire loop pushes back easy into box. Solid n m not quite as easy . What about loop the bare ground, it has turned up taps on each side of screw . Seems to me it is better ground connection not to cut it. I dont think any would could call a non current conductor a fed thru. In case like Iwire there will be a loop at each switch location instead of single conductor
Not sure I follow, why does 5 light fixtures always require more than 1 circuit ? :-?
Not sure I follow, why does 5 light fixtures always require more than 1 circuit ? :-?
Not sure I follow, why does 5 light fixtures always require more than 1 circuit ? :-?
I don't like switches wired that way because it makes it harder to replace the switch down the road. The loop feed & ground wires often get tangled in with others, ground especially, got to watch it for shorting. I like a separate feed for each switch.I dont follow , there is no difference except instead of a hot jumper ran to each switch and wire nut to hot in , the same hot in just loops to each switch. why would some one else go back and cut it off with switches in ? If it is cut off before then I wire it your way . A 3 way gets a hot the same way , and the two travelers on the other screws to the 14 /3 with neutral , dont they know where the 3 way goes , no matter if the hot is long or short :-?
What I am saying is there's a good chance the long hot will get cut off by mistake at the trim, as the switches are installed. Do as you please, it's none of my business. I prefer to make it as mindless as possible to minimize mistakes.
I didn't read thru the whole thread so forgive me if somebody else mentioned this: Good for you George, but anyway the practice was pretty popular for us how do we say? Old Fogey's. So you young pups might cut the long hot off but I bet no oldtimers (are there any in the field besides me anyway?) would make that mistake very often....![]()
I didn't read thru the whole thread so forgive me if somebody else mentioned this: Good for you George, but anyway the practice was pretty popular for us how do we say? Old Fogey's. So you young pups might cut the long hot off but I bet no oldtimers (are there any in the field besides me anyway?) would make that mistake very often....![]()