Extraneous Conductive Parts above False Ceiling
TMMB
EGYPT
Electrical Manager
My question is , is there any article in NEC support the following:
all extraneous conductive parts of the building such as metallic water pipes, drain pipes, other services pipes and ducting, metallic conduits and raceways, cable trays and cable Armour are to be connected to nearest earthing terminals by equipotential bonding conductors. cross section of the protective bonding conductor is not to be less half that of the protective conductor connected to respective earthing terminal and min. 4 mm2
please, if there any article in NEC support the above statement, let me know
if not, so i would like ask: is it required to connect any metallic conduits/water pipes which installed above false ceiling to connect to earth terminals?
No section in the NEC requires anything so broad or all encompassing above a ceiling.
Metal water pipe systems are required to be bonded once
Metal conduits containing circuit conductors are required to be grounded.
Cable armor would be grounded at each end by the metal enclosure it is connected to.
As was mentioned it sounded like a design specification.
Many thanks for you feedback
if there is no section in NEC talk about that, so based in what you said the following:
And building steel would be bonded as well.
finally, is it required or not to connect all metal bodies such above false ceiling as water pipes, firefighting pipes, A/C ducts,.....??
Read part V of article 250, it covers what your questions. Parts IV, VI, and VII could help too.
Roger