I have a 3” RMC conduit straight run with a support approximately 6’ from a 3”, 90 degree factory elbow. This appears to be non-compliant with NEC 344.30(A) - i.e. a support will need to be added within 3’ of the 90 degree elbow.
And, 314.23(E) exception seems to be written only for conduit bodies - and factory elbows are not included.
Is this correct?