Factory 90 degree elbow and conduit bodies support locations

Merry Christmas

Dale001289

Senior Member
Location
Georgia
I have a 3” RMC conduit straight run with a support approximately 6’ from a 3”, 90 degree factory elbow. This appears to be non-compliant with NEC 344.30(A) - i.e. a support will need to be added within 3’ of the 90 degree elbow.
And, 314.23(E) exception seems to be written only for conduit bodies - and factory elbows are not included.
Is this correct?
 
With pretty much all non flexible type raceways supports are needed within 3 feet of cabinets, boxes conduit bodies or other terminations of the raceway. Couplings, bends, elbows (whether a factory elbow or a field made bend) are considered part of the raceway run when considering support requirements.
 
You do not need a support at each coupling and you do not need a support at a bend per the code.
The code may not require it, but it's probably best practice to have a support nearby your bends, so that you don't have a 5 ft cantilever from both of the nearest supports. Job specs may call for a maximum distance from the bend on both sides, to the nearest support. If practical, a diagonal support at the midpoint also does the trick.

If it's my choice to specify it, I'd limit this distance to 30% of an allowable span of the conduits size-and-type on both ends of a standalone bend that's 45 degrees or greater, based on beam mechanics. For saddle bends and offset/return bends, that add up to net zero change in direction, I'm OK with the standard spans from the NEC, with no special attention given to the bend.
 