Customer bought a brand new 25 hp three phase 480 volt air compressor. Paid the distributor/dealer an extra $380 for them to convert it to 480. Has two different nameplates, one says 220 volt, while a sticker was added “440 volt”. Bumped it to check rotation, all good. Runs for two days, the electronic overload relay explodes. Salesman wants a picture of the starter to see if his guys actually converted it. Ok…then I seen how he could tell, they brought all of the motor leads to the bottom of the starter, where they split out the windings, and changed the taps, wrapping them in some tape. They forgot to change out the electronic overloads!